Hey Chris - Matt Hoppes suggested I ask you about the temperature on the inside of steel water towers. We have a situation that may require us to use one as a repeater, and we have no experience with them at all. Just need to make sure the equipment will not cook in there. Thanks
The tower looks like this:
Water Tower Temperature
-
sirhc - Employee
- Posts: 7416
- Joined: Tue Apr 08, 2014 3:48 pm
- Location: Lancaster, PA
- Has thanked: 1608 times
- Been thanked: 1325 times
Re: Water Tower Temperature
We were just reviewing our cabinet Temps from last year.
A similar water tank with the equipment mounted in the base of the tower inside that garage door.
Diller Ave Tank had a hottest recorded cabinet temperature of 82.4F yet we had outside air temperatures of near 100F.
The box is vented with a fan and the water in the tank cools the air as the water is suspended above and the cool air drops. Water temperature from the ground that is pumped into the tank is 52F or below.
There is normally a condensation pan / trap that is suspended below the water containment area to catch the water droplets that form on the bottom of the tank. So long as the door are kept closed the inside temperature is less than outside.
A similar water tank with the equipment mounted in the base of the tower inside that garage door.
Diller Ave Tank had a hottest recorded cabinet temperature of 82.4F yet we had outside air temperatures of near 100F.
The box is vented with a fan and the water in the tank cools the air as the water is suspended above and the cool air drops. Water temperature from the ground that is pumped into the tank is 52F or below.
There is normally a condensation pan / trap that is suspended below the water containment area to catch the water droplets that form on the bottom of the tank. So long as the door are kept closed the inside temperature is less than outside.
Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.
-
wayneorack - Experienced Member
- Posts: 129
- Joined: Thu Sep 04, 2014 12:16 pm
- Location: San Angelo, TX
- Has thanked: 188 times
- Been thanked: 64 times
Re: Water Tower Temperature
Looks like an ambulance. Is that what happened to the competition?
- Zerofail
Re: Water Tower Temperature
Yes, that does look like an ambulance :)
CHris, thanks for the info
CHris, thanks for the info
- turtles2
Re: Water Tower Temperature
What about cold weather? I'am talking 0 to to -20 F. Dose it get that cold over where you are at?
-
sirhc - Employee
- Posts: 7416
- Joined: Tue Apr 08, 2014 3:48 pm
- Location: Lancaster, PA
- Has thanked: 1608 times
- Been thanked: 1325 times
Re: Water Tower Temperature
turtles2 wrote:What about cold weather? I'am talking 0 to to -20 F. Dose it get that cold over where you are at?
THe water works in reverse in the winter as the water is now 52F so it is warmer inside the base then outside.
We got down to just below 0F this winter but inside the tower was an east 20+ degrees warmer
Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.
-
rebelwireless - Experienced Member
- Posts: 607
- Joined: Mon Sep 01, 2014 1:46 pm
- Has thanked: 31 times
- Been thanked: 136 times
Re: Water Tower Temperature
or well within the operating range of a wispswitch ;)
-
mayheart - Experienced Member
- Posts: 166
- Joined: Thu Jan 15, 2015 1:42 pm
- Location: Canada
- Has thanked: 43 times
- Been thanked: 40 times
Re: Water Tower Temperature
No problems here.
Co-located in several water towers.
One tower we have our equipment pretty close to the room they do chlorine mixing. Gotta replace the switch every 2-3 years due to corrosion.
Co-located in several water towers.
One tower we have our equipment pretty close to the room they do chlorine mixing. Gotta replace the switch every 2-3 years due to corrosion.
-
rebelwireless - Experienced Member
- Posts: 607
- Joined: Mon Sep 01, 2014 1:46 pm
- Has thanked: 31 times
- Been thanked: 136 times
Re: Water Tower Temperature
mayheart wrote:
One tower we have our equipment pretty close to the room they do chlorine mixing. Gotta replace the switch every 2-3 years due to corrosion.
can you seal up the box a bit and draw in some outside air? Positive pressure in the box w/ outside (or 'clean') air should solve your corrosion issue.