WS-10-250-AC reporting too much wattage

pointrow
Member
 
Posts: 1
Joined: Tue Mar 08, 2016 12:31 pm
Has thanked: 0 time
Been thanked: 0 time

WS-10-250-AC reporting too much wattage

Thu Jul 06, 2017 5:25 pm

hey guys, i have one site of a few using 250-ac switch that has a combo of older m5 rockets and 5ghz ac rockets this is only site with ac rockets using the switch notice the wattage on ac radios close to 40 watts each as well as the m5 rockets... is this a firmware issue? running 1.4.7 board D 1.4.6 same thing

Julian
 

Re: WS-10-250-AC reporting too much wattage

Thu Jul 06, 2017 7:36 pm

Not a firmware issue, but indicative of a grounding issue.

The current sensors are the coal mine canaries of your switch- they're the easiest path to chassis/earth ground for stray electrons, so they're the first to blow when there's a problem.

Ask sirhc, he'll bend your ear about grounding- l usually just recommend you search this forum for the word grounding and keep reading until grounding no longer looks like a word, there's plenty of good stuff around.

Anyway, you can RMA your switch if you like, we can repair this level of ground current damage reasonably inexpensively.

User avatar
sirhc
Employee
Employee
 
Posts: 7415
Joined: Tue Apr 08, 2014 3:48 pm
Location: Lancaster, PA
Has thanked: 1608 times
Been thanked: 1325 times

Re: WS-10-250-AC reporting too much wattage

Thu Jul 06, 2017 10:48 pm

Support is handled on the Forums not in Emails and PMs.
Before you ask a question use the Search function to see it has been answered before.
To do an Advanced Search click the magnifying glass in the Search Box.
To upload pictures click the Upload attachment link below the BLUE SUBMIT BUTTON.

Return to General Discussion

Who is online

Users browsing this forum: No registered users and 18 guests