Inrush Current WS-8-150-DC
Posted: Thu Oct 19, 2023 12:57 pm
Typically we are using a 24V setup and connecting the switch to the batteries (as recommended ).
I want to be sure that the circuit breaker is sized appropriately (we've been successfully using 5A based on 150W being 5.2A to 6.3A within the typical battery voltage range and the fact that we typically use < 50W total including 10W for the switch).
Searched and didn't find a number for what the inrush current is for the WS-8-150-DC.
It would also be nice to know what it is for the WS-12-250-DC as well.
I want to be sure that the circuit breaker is sized appropriately (we've been successfully using 5A based on 150W being 5.2A to 6.3A within the typical battery voltage range and the fact that we typically use < 50W total including 10W for the switch).