Groundings recap /tips:I always add 1 or 2 NEW grounding rods to older existing electrical services and clean up and corrosion
If electrical service ground rods are too far from tower then follow this post:
viewtopic.php?f=17&t=1786&start=30#p13447Make sure you run a heavy #2 ground bonding wire between electrical service ground rods and tower ground rods.
Earth Ground current is the #1 cause of WISP equipment damage NOT ESD and surges.
We also repair UBNT and MIMOSA radios and we see the same damage to those units as our switches when there is poor grounding.
For info on repairing UBNT and MIMOSA radios read this post:
viewtopic.php?f=21&t=2827#p19482Here are some good posts on grounding:viewtopic.php?f=30&t=2786&p=19279#p19279viewtopic.php?f=30&t=1816viewtopic.php?f=30&t=188viewtopic.php?f=17&t=1786&start=30#p13447viewtopic.php?f=30&t=1429