This sounds a lot like the issue I had with Bareville water tank and in that case I think the console was non functional.
However I would like to note that that switch at Bareville Water Tank is still in service today and all we did there was replace the UPS and replace the Ethernet cable run to the business with fiber and no more issues in 18 months.
Since this is a DC site and I assume you have to Ethernet cable running to another building I would suspect a grounding issue.
Is the tower grounded by several ground rods?
Is there 2 ground rods on the electrical service?
Is the tower ground system bonded to the electrical service ground system?
Do you have a dedicated ground wire run up to the radios and is the Ethernet cable a longer path than the intended ground wire path?
Read these 2 post very closely.viewtopic.php?f=30&t=188viewtopic.php?f=30&t=1429If this tower is up on a hill and is exposed to high winds you can be getting static charges going down your Ethernet cables.
So many people do not understand how important a good grounding system is which is why cellular companies spend so much money on their grounding systems and their towers do not take hits all the time. Think about it, a cellular company has tens of thousands of towers and if they took damage like most WISPs do from poor grounding your cell coverage would be dropping all over the place.
Good grounding is the key to a trouble free tower as you have surges, ESD, Static, and ground potential shift all of which can either damage your equipment or play havoc on their stability.
MAKE SURE YOU HAVE EARTH GROUND CONNECTED TO THE DC SWITCH CHASSIS AS THAT IS THE ONLY SOURCE OF GROUND FOR THE SWITCH OTHER WISE YOUR ESD ETHERNET CABLE IS USELESS. AND MAKE SURE ALL GROUNDING SYSTEMS ARE BONDED TOGETHER.