DC glory
Posted: Sat Jan 02, 2016 4:20 pm
Hi guys,
I've recently discovered the benefits to running sites purely on DC, and am now looking to design a template for powering all of our on-grid sites with a pair of 12V AGM batteries in series. The theoretical run time you can achieve running off just a couple of small AGM batteries is quite impressive. A big beefy liebert 1KVA $1k UPS would power a medium sized site (consuming under 100W) for under 2 hours.
Here's what I'm currently thinking..
For small sites with 3 Rocket APs (worst-case 10 watts each), a AirFiber-X backhaul (worst-case 15 watts), a WS-250-DC and mikrotik router (worst-case 20 watts combined), a total power consumption 65W, I could get 20 hours of run time if the grid goes out with the following equipment:
Just thought I'd share why I'm excited for fully DC sites in our nework. 20 hours is long enough in most cases for the grid to come back on, and we could probably squeeze more time out of the batteries and the 12v input converter. For larger sites, we could use higher-capacity batteries, with the goal of reaching a minimum 24-hours runtime when the grid goes off.
If you guys have any other suggestions, I'd love to hear them :)
I've recently discovered the benefits to running sites purely on DC, and am now looking to design a template for powering all of our on-grid sites with a pair of 12V AGM batteries in series. The theoretical run time you can achieve running off just a couple of small AGM batteries is quite impressive. A big beefy liebert 1KVA $1k UPS would power a medium sized site (consuming under 100W) for under 2 hours.
Here's what I'm currently thinking..
For small sites with 3 Rocket APs (worst-case 10 watts each), a AirFiber-X backhaul (worst-case 15 watts), a WS-250-DC and mikrotik router (worst-case 20 watts combined), a total power consumption 65W, I could get 20 hours of run time if the grid goes out with the following equipment:
- 2x 12v 55AH AGM battery in series for 55AH @ 24V (for a total of approx. 1320 watt-hours) ($320 CDN)
- 1x DROK 600W 12-60V input 12-80V output DC-DC converter for regulated 48v to power WS-250-DC. It's good to power up to 240W with 24V input, more than we'll ever draw at a site. (not sure what conversion efficiency will be) ($40 CDN)
- 1x NOCO G7200 24v battery charger/maintainer/reconditioner ($110 CDN)
Just thought I'd share why I'm excited for fully DC sites in our nework. 20 hours is long enough in most cases for the grid to come back on, and we could probably squeeze more time out of the batteries and the 12v input converter. For larger sites, we could use higher-capacity batteries, with the goal of reaching a minimum 24-hours runtime when the grid goes off.
If you guys have any other suggestions, I'd love to hear them :)