Grounding Grounding Grounding
Posted: Sat May 27, 2017 11:35 am
On direct strikes (tower hit) no, grounding will probably not save you but most damage to WISPs is not from direct strikes, or ESD (near strikes). Most damage is from ground current and sometime static discharges.
Ground current is the #1 cause of damage to WISP equipment and proper grounding and bonding all grounds together will most definitely save you.
Making sure electrical service ground rods are bonded to tower ground rods is VERY IMPORTANT. In fact making sure the Electrical service ground rod is in good condition each spring, corrosion free and TIGHT in the ground. If you have less than 2 ground rods on the electrical service add a second bonded to the first at least 4-6 feet away and if you have 2 ground rods and either are loose add a 3rd.
I also go to the pole where the transformer is and add a second ground rod there as often the utility company simply set a short ground rod in the same hole while setting the pole which is useless. Come a few inches off the pole and drive in a 5/8" 8-10 foot ground rod. Strip the #6 copper insulation off the wire coming down the pole to their ground rod and use a split bolt to secure #6 copper wire to your new ground rod with a copper acorn.
ESD is rare but Static and ESD protection is handled the same way. Make sure you run a #2 green wire up the tower from your tower's main ground bus bar at the base of the tower to an insulated ground bus bar near your antennas and then run #6 green to each antenna mount.
Make sure all ground wires run down hill never uphill, pretend they are pipes and if you put water in the top and make sure the wires would drain empty.
Static builds up on the antennas when wind blows across them at just the right humidity or dew point which is what happens in the spring, summer, and fall as it is normally hot and a cool front comes in and temperature drops rapidly with high winds which when the dew point hits the right amount huge amounts of static are generated on the tower and that static charge will look for a path to ground and you do not want the path chosen to be your Ethernet cable. This is another reason to always want a 10' or more service loop on your Ethernet cable at the top so the cable path is longer and less attractive than the intended ground wire path. This is also the same type of protection to help with ESD but as I said ESD is rare but people constantly confuse ESD and or storm damage with ground current and static damage.
Money and time spent on grounding is money and time well spent
Ground current is the #1 cause of damage to WISP equipment and proper grounding and bonding all grounds together will most definitely save you.
Making sure electrical service ground rods are bonded to tower ground rods is VERY IMPORTANT. In fact making sure the Electrical service ground rod is in good condition each spring, corrosion free and TIGHT in the ground. If you have less than 2 ground rods on the electrical service add a second bonded to the first at least 4-6 feet away and if you have 2 ground rods and either are loose add a 3rd.
I also go to the pole where the transformer is and add a second ground rod there as often the utility company simply set a short ground rod in the same hole while setting the pole which is useless. Come a few inches off the pole and drive in a 5/8" 8-10 foot ground rod. Strip the #6 copper insulation off the wire coming down the pole to their ground rod and use a split bolt to secure #6 copper wire to your new ground rod with a copper acorn.
ESD is rare but Static and ESD protection is handled the same way. Make sure you run a #2 green wire up the tower from your tower's main ground bus bar at the base of the tower to an insulated ground bus bar near your antennas and then run #6 green to each antenna mount.
Make sure all ground wires run down hill never uphill, pretend they are pipes and if you put water in the top and make sure the wires would drain empty.
Static builds up on the antennas when wind blows across them at just the right humidity or dew point which is what happens in the spring, summer, and fall as it is normally hot and a cool front comes in and temperature drops rapidly with high winds which when the dew point hits the right amount huge amounts of static are generated on the tower and that static charge will look for a path to ground and you do not want the path chosen to be your Ethernet cable. This is another reason to always want a 10' or more service loop on your Ethernet cable at the top so the cable path is longer and less attractive than the intended ground wire path. This is also the same type of protection to help with ESD but as I said ESD is rare but people constantly confuse ESD and or storm damage with ground current and static damage.
Money and time spent on grounding is money and time well spent